Welcome to the Arc Flash Forum - A Global Community for Arc Flash and Electrical Safety! Join our global community and become part of the conversation Create your user profile page - Tell us about yourself! Add your profile photo Post questions and responses Contribute your articles to the Library Receive weekly email updates "Like" other member's posts ...and much more! If you have any questions, please feel free to contact us at 1-800-874-8883 Thanks for stopping by! - Jim Phillips Learn More About the Arc Flash Forum Here Login Trouble? Lost Password? [Login Help]

Question on info on a label


Discussion in 'Arc Flash Labels' started by glen1971, Dec 2, 2010.

Weekly Update Share this Site with others


Subscribe

Subscribers will Receive a 33 page Arc Flash Hazard Calculation Guide. I was out installing glen1971 labels today on some
Sparks Level

sites and am now looking for some help with how to interpret the label.. Mainly a "How would you read it"... The Labels are: - for a 480 volt MCC

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 2 of 7

- the Arc Flash Rating for the Line and Load side of the Breaker are the same (48.0 cal/cm2) and as such there is "no PPE available". Now my question... I have the LINE side values clear as mud, but does the LOAD side include the Load Side of the Main Breaker, the bus, and the Line Side of the disconnects in the starters? Or does it include the Load Side of the Main Breaker, the bus, the Line Side of the disconnects in the starters, the starter, and all connections up to the LOAD wires (Motor Feeder, Transformer Feeder, etc)? Or is it only the Load side of the Main breaker and the bus? NOTE: Not looking to breakdown the Arc Flash study, but just how to read the label. We may be looking into revisiting some of the sites in the study, and possibly adding Arc Reducing Controls.
glen1971, Dec 2, 2010 #1

SCGEng1

Low voltage MCCs have been a continuing

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 3 of 7

Sparks Level

problem for us, specifically when they return high incident energy values. Weve been treating the MCC Bus, the individual starter buckets, and all the parts within (MCP, Starter, Overloads, etc) all at the value calculated for the MCC Bus. Weve debated the typical molded case breaker within the bucket should be very fast resulting in a very low hazard level for load side faults (i.e. working within the bucket). However, we see the problem being the protective device (the molded case breaker) is within the working location, in other words, the breaker which could quickly clear the fault is within the same location you are working. Another concern is there's typically no means to restrict access to the line side of the breaker. Weve seen some examples of individuals attempting to remove a breaker from a starter bucket, while the bucket is still engaged to the MCC bus, resulting in a very bad outcome.

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 4 of 7

Therefore we assume the next device upstream as the primary clearing device for activities within the starter bucket. This is either the MCC main or the supply transformer high side over current protection if the MCC does not have a main breaker (most of ours do not). We typically look at engineering solutions to lower the incident energy potential to within Level 2 PPE for the entire MCC whenever possible. For working locations supplied from the MCC we do take credit for the protection within the starter bucket.
SCGEng1, Dec 3, 2010 #2 SCGEng1 said:

JBD
Sparks Level

Therefore we assume the next device upstream as the primary clearing device for activities within the starter bucket. This is either the MCC main or the supply transformer high side over current protection if the MCC does not have a main breaker (most of ours do not).

This is what we do also.

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 5 of 7

JBD, Dec 3, 2010 glen1971 said:

#3

Robertefuhr
Sparks Level

....LOAD side include the Load Side of the Main Breaker, the bus, and the Line Side of the disconnects in the starters? Or does it include the Load Side of the Main Breaker, the bus, the Line Side of the disconnects in the starters, the starter, and all connections up to the LOAD wires (Motor Feeder, Transformer Feeder, etc)? Or is it only the Load side of the Main breaker and the bus?.... QUOTE] The AF values for the load and line side device could be the same because both the MCC main and upstream (from the MCC) breakers are the same mfg/type and have identical settings. Another reason could be the upstream protective device will trip before the main breaker (called mis coordination option in SKM.) This option will cause SKM to use the upstream device to determine the energy values instead of the slower Main breaker. This is why we put the protective device that was used to determine

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 6 of 7

the energy level our labels.


Attached Files:

AF La be l.j pg File KB Vie 23

Robertefuhr, Dec 3, 2010 #4

glen1971
Sparks Level

Thanx for the posts... With the rating on the LOAD side of the Bus I assumed that it carried through to the LINE side of the breaker. SCGEng1 made a good point and I think that will probably lead to a revist on the Arc Flash Study and possibly the installation of Arc Reducing Devices.
glen1971, Dec 4, 2010 #5 glen1971 said:

glen1971
Sparks Level

Thanx for the posts... With the rating on the LOAD side of the Bus I assumed that it carried through to the LINE side of the breaker. SCGEng1 made a good point and I think that will

http://arcflashforum.brainfiller.com/threads/1415/

12/18/2013

Question on info on a label | Arc Flash Forum

Page 7 of 7

probably lead to a revist on the Arc Flash Study and possibly the installation of Arc Reducing Devices.

After consulting the client they are going to be revisiting the study and confirming the numbers.. Then looking at how to reduce the Incident Energy to one where it can be worked on. The conclusion they came to was that the LOAD side of the Main Breaker fault calculations carry through each starter to the T1/T2/T3 terminals, as the starter breaker won't clear a fault quick enough to lower the energy levels..

http://arcflashforum.brainfiller.com/threads/1415/