WHY SOLAR AND HYBRID SOLUTIONS HAS BECOME THE PREFERRED SECOND SOURCE OF ENERGY February 2010
www.eltekvalere.com -1-
Traditionally, operators would use AC Generator Set (Gen-set) to provide either the primary or supplemental site power needs given they are relatively cheap and easy to install. However, given Gen-sets typically run on fossil fuels, it also makes them expensive to run, noisy and harmful to the environment.
With the growing focus on reducing OPEX and being more environmentally responsible, operators are now looking for more cost-effective and cleaner alternative energy solutions. This is highlighted by the increasing number of installations that are using solar energy to provide power to their telecommunication sites.
This white paper has therefore been prepared to describe in detail the technologies involved with Solar Power solutions and how they can be utilized to achieve significant OPEX savings.
-2-
TABLE OF CONTENT
LOWERTHEOPEXWITHALTERNATIVEENERGY.......................................................................................2 WHYSOLARPOWERHASBECOMETHEIDEALSECONDSOURCEOFENERGY,EITHERASAUTONOMOUSORHYBRIDSOLUTIONS ...................................................................................................................................................................2 TABLEOFCONTENT..................................................................................................................................3 TERMINOLOGY.........................................................................................................................................4 I. ABBREVIATIONS..............................................................................................................................4
1.SOLARPOWER.....................................................................................................................................5 1.1OFFGRIDSITEPOWERCONFIGURATION........................................................................................................5 1.2HARVESTINGSOLARENERGY.......................................................................................................................6 1.2.1 Energyconversion...................................................................................................................6 1.2.2 Sunpositiontrackingsystems ................................................................................................7 . 1.3BATTERYTECHNOLOGY..............................................................................................................................8 2.HOWITWORKS....................................................................................................................................9 2.1DIESELGENERATOR,GENSET....................................................................................................................9 2.1.1OPEXintensive.............................................................................................................................9 2.1.2CAPEXfavourable.......................................................................................................................10 2.2CYCLEDDIESELGENERATOR......................................................................................................................10 2.2.1CAPEXintensive..........................................................................................................................11 2.2.2OPEXeffects...............................................................................................................................11 2.3.ADDINGSOLARENERGY..........................................................................................................................11 2.3.1Solardata...................................................................................................................................11 2.4SUNPATHFIXEDTILTANDTRACKINGSYSTEMS..........................................................................................13 2.4.1Fixedtilt......................................................................................................................................13 2.4.2Fixedtiltseasonaladjustment.................................................................................................13 2.4.3EWtracking ..............................................................................................................................13 . 2.4.4Dualaxistracking,addingNStracking.....................................................................................14 2.5PVPANELCHARACTERISTICS......................................................................................................................15 2.6.CHARGECONTROLLERS............................................................................................................................16 2.6.11stgeneration,directchargecontrol..........................................................................................16 2.6.22ndgeneration,MPPTcharger ...................................................................................................16 . 2.6.3.3rdgeneration,MPPTchargerw/galvanicbarrier....................................................................16 2.6.4EltekValereSolarchargerFlatpack2HESolar........................................................................17 2.7BATTERIES.............................................................................................................................................17 2.7.1StandbyAGM..........................................................................................................................17 2.7.2OPzV...........................................................................................................................................17 2.7.3OpzS...........................................................................................................................................18 2.7.4NiCd............................................................................................................................................18 3.INTEGRATINGPVPANELSINTOTHEPOWERSYSTEM........................................................................19 3.1ADDINGSOLARTOASTANDARDSYSTEM.....................................................................................................19 3.2ADDINGSOLARTOCYCLICAPPLICATION.......................................................................................................19 3.3OPTIMIZINGTHEHYBRIDCYCLICAPPLICATION...............................................................................................19 4.CASESTUDY.......................................................................................................................................21 REFERENCES...........................................................................................................................................23
ALTERNATIVE ENERGY SOLUTIONS OFF GRID
-3-
TERMINOLOGY
Chapter 1 will introduce various site solution configurations for an off grid site and compare the relative cost and performance of each of the major technologies available. For easy understanding, the comparison is displayed in a table matrix format, with the following symbols being used to represent the different expenditure or performance levels. Briefly stated; the more shaded the circle, the better the assessment. Symbol Capex / Opex Minimal / No cost Cost effective Acceptable Expensive Very Expensive Performance Excellent Very Good Satisfactory Below Average Unacceptable
I. ABBREVIATIONS
The following lists the abbreviations used in this paper. ATM BTS DOD EMC HE MPPT PV SOC STC : Standard Atmosphere symbol (unit of pressure). : Base Transceiver Station : Depth of Discharge : Electro-Magnetic Compatibility : High Efficiency : Maximum Power Point Tracking : Photo Voltaic : State Of Charge : Standard Test Conditions
-4-
1. SOLAR POWER
The first step in finding out how Solar Power can reduce OPEX is to understand what technologies are used, how they can be combined and what benefits and limitations each option has.
-5-
The following table indicates the typical assessment of each of the basic site configuration. Configuration Gen set only Cycled Gen set Hybrid Solar only CAPEX OPEX CO2 Emission Site down Risk
-6-
d) Eltek Valere Uses an high-efficient isolated DC-DC converter with MPPT functionality. The following table indicates the performance of each technology as a charge controller for solar power on a telecom site.
Surge protection
Telecom specification ? ? ?
1.2.2 Sun position tracking systems The amount of energy collected by a PV panels depends on the intensity of sun beams hitting the front of the panel. As the suns path varies east-west during a day and northsouth with the seasons, tracking systems can be used to adjust the panels orientation towards the sun, thus helping to maximize the energy harvested by the PV panel. If sun tracking is not used, then the PV panels are fixed into the most optimal position based on the sites latitude from the equator. Technology Fixed Seasonal adjusted 1-axis 2-axis CAPEX OPEX Reliability Energy utilization
-7-
AN ELTEK VALERE WHITE PAPER
CAPEX
OPEX
Cycling
Temperature Environment
-8-
2. HOW IT WORKS
The previous chapter outlined the pros and cons of the main building blocks when powering off grid telecom sites. This chapter will focus in detail on the discussed building blocks.
This means that typically a generator will be operating for most of its operation time to supply a load much less than its rated capacity. Typically as low 10-20%. As seen from Figure 1, when a generator is operating against a small load, the operating efficiency is far from optimum.
2,5
1,5
0,5
0 0 10 20 30 40 50 60 70 80 90 100
Load [%]
High maintenance cost Figure 1 Generator efficiency Diesel generators are maintenance intensive, resulting in frequent site visits. The yearly maintenance cost can easily exceed the initial investment. Summarized the OPEX disadvantages are: Working life is typically at low efficiency, less kWh pr litre fuel. Large CO2 emissions Maintenance and service intensive -9AN ELTEK VALERE WHITE PAPER
2.1.2 CAPEX favourable When operating a off-grid site mainly on a gen-set however, the site installation and complexity is quite low, as is the CAPEX investment. CAPEX advantages are : Generators are relatively cheap compared to many other off-grid power sources. Small battery bank with standard batteries A standard power controller can be used
...n
n+1
discharge
cha rge
discharge
cha rge
discharge
charge
24h
?h
It this configuration, the battery bank changes from being a backup energy source in a site with a continuously running diesel generator, to play a more active role in powering the site. As the role of the batteries has changed, the battery technology used must also be updated. Standard lead-acid batteries are designed to serve as a stand-by backup, and may only survive 200-300 cycles, depending of DOD in each cycle. In this case, a daily cycling period using standard batteries would result in need of replacement of the batteries in less than a year.
- 10 -
2.2.1 CAPEX intensive Comparing only the investment cost for a cycled generator vs. a traditional site works in disfavour of a cycled site: The need for intelligent start and stop of the generator increases complexity of the controller. The batteries designed for cyclic application are generally more expensive than standby batteries. The Ah size of the battery bank needs to be increased to provide discharge time and serve as backup when a normal discharge cycle has ended.
2.2.2 OPEX effects However, when also taking into account the OPEX savings realised during the expected site lifetime, the overall business case tends to strongly favour a cycled Gen-set solution in nearly all situations. Gen set operates at higher efficiency, more energy pr. litre diesel. Reduced operating hours means less daily fuel usage and less frequent service related site visits.
- 11 -
The available energy for a specific location can then be analyzed. Figure 4 shows an example of an average monthly energy profile, whilst Figure 5 shows an estimated daily energy graph.
Solar data are historical data, typically 10 years average. Predicting the exactly amount of future solar energy on daily basis is not possible, but the historical data gives a good indication of what can be available as an average.
- 12 -
AM
PM
AM
PM
AM
PM
2.4.2 Fixed tilt seasonal adjustment A variant of the fixed tilt adds the possibility of letting the tilt is manually adjusted. Depending on the regularity of site visits, the tilt can be adjusted to increase the monthly or seasonally collected solar energy.
2.4.3 E-W tracking An east west tracker is a 1-axis automated tracker that follows the suns position from east to west during the day. The tracking will only increase the amount of direct radiated energy and the mix of solar radiated energy (direct diffuse reflected) determines how large the total gain is. Generally a 1-axis tracker will be more expensive than a fixed, it will have moving parts that are a single point of failure, and it may also require maintenance. In addition, the tracking systems will use power to operate, thus reducing the overall gain it may provide.
AM
PM
AM
PM
AM
PM
- 13 -
2.4.4 Dual axis tracking, adding N-S tracking In a dual axis tracking system, the daily and seasonal north-south variation of the suns position is also tracked. The gain is stated to be as high as 40% compared with a fixed installation during summer by manufacturers, but the real gain will depend on the mix of the solar energy (direct diffuse reflected) available. The higher the share is of diffuse irradiation, the less is the gain from a tracking system. The cost of a dual axis tracker is higher than the 1-axis tracker, and will have more moving parts than the 1-axis tracker.
Summer Spring/Autumn
Winter
Summer Spring/Autumn
- 14 -
Figure 7, the available power varies significantly with irradiation and panel temperature.
1000W/m
Direct
200W/m
800W/m
Direct
200W/m
- 15 -
Figure 7, a battery voltage of typically 24-25V will reduce the output power to ~70% of the maximum available power. So even though the direct charge controller has low losses (only conduction losses and junction box diode losses), the utilization of the PV panel is poor. Immunity to lightning pulses is low, as there is a direct galvanic connection from the PV panels into the telecom system. Adding surge protection devices on this equipment will have limited effect. 2.6.2 2nd generation, MPPT charger The evolution from 1st to 2nd generation charge controller solves the issue of the battery voltage determining the operation point of the PV panels. A dcdc converter enables the possibility to let the output voltage of the charger to be independent from the PV voltage. The charger needs intelligence in form of a microcontroller etc. to perform Maximum Power Point Tracking (MPPT) algorithms. With a proper algorithm the charger should be able to operate at close to 100% PV panel utilization. The topology of dcdc converter is normally one stage non isolated. This topology will give conversion efficiency in the range of 92-96%. The charger has the same weakness as 1st gen, direct galvanic connection from the PV panels into the telecom system, and limited effect of surge protection devices. 2.6.3. 3rd generation, MPPT charger w/galvanic barrier The 3rd inherits the MPPT functionality of the 2nd generation equipment and solves the issue with galvanic barrier by introducing a 2nd stage in the dcdc converter. The added stage affects the efficiency of the charger; it decreases to typically 86-91%.
- 16 -
In combination with a correctly sized surge protection, a 3rd generation charge controller will give good surge protection for the telecom load. 2.6.4 Eltek Valere Solar charger Flatpack2 HE Solar The Eltek Valere solar charger has all the functionality of the 3rd gen equipment, but due to the patented HE technology the efficiency is raised to typically 96%. The Flatpack2 HE Solar Charger is a product derived from the standard HE technology, and follows the normal telecom standards with respect of safety, EMC, electrical characteristics and transportation. The converter is an extension to the standard telecom range offered by Eltek Valere, that all share the same control interface.
2.7 Batteries
As mentioned in chapter 1, a large part of configuring a hybrid site is choosing the optimum battery technology. To find the best fitted technology several parameters must be evaluated, such as CAPEX, OPEX, ambient temperature, size, expected lifetime, weight, and fright. 2.7.1 Standby AGM Standby lead-acid batteries are designed to work as a backup source, and not in cyclic applications. There they will only survive a limited number of discharge cycles, and if used in cyclic application it will lead to frequent battery replacement. 2.7.2 OPzV The abbreviation OPzV is German, and refers to German standard DIN 40742. O: Ortsfest = Stationary Pz: Panzerplatte = Tubular plate (+) V: Verschlossen = Valve regulated The batteries are sealed gel based. They are slightly better with respect of ambient temperature than regular gel batteries but also more expensive. The lifetime of the battery is a function of DOD, and the number of cycles is stated in the datasheet. Typically the number of cycles can be 1200 cycles at 60% DOD at 20C.
- 17 -
2.7.3 OpzS The abbreviation OPzS is German, and refers to German standard DIN 40737. O: Pz: S: Ortsfest = Stationary Panzerplatte = Tubular plate (+) Spezial = Special, Fluid electrolyte with special seperator
OPzS is a flooded battery designed for cyclic application. They are better than OpzS with respect of ambient temperature, but as they are flooded they will require refilling at regular basis. The refill interval and lifetime of the battery is a function of DOD and temperature. The number of cycles is stated in the datasheet. Typically the number of cycles can be 1200 cycles at 60% DOD at 20C Transport restrictions of the product may exist, and must be considered when planning a project. 2.7.4 NiCd The characteristics of NiCd batteries are specified in DIN 61427. An advantage of nickel cadmium is the batterys ability to tolerate extremes in heat and cold without a degradation of its useful life. NiCd batteries can be charged at a higher rate than lead-acid batteries. NiCd has more cycles at shallow DOD compared with an OPzV/OPzS battery, but less at deeper DOD. The number of cycles is stated in the datasheet The NiCd requires water topping at an interval given by temperature and DOD. The Cadmium in the battery is a toxic, and special recycling arrangements must be in place in the region of deployment.
- 18 -
LOAD
AC/DC
A typical charge/discharge cycle involves the phases shown in Figure 9. From midnight until sunrise the load is supplied by the batteries, and thus the batteries are discharged. From after dawn the PV panels delivers energy, and after awhile it is sufficient to charge the batteries. At sunset the load is again supplied by the batteries, and they are again discharged. At a given time or DOD the generator starts, and supplies the load and charges the batteries. At a DOD above 0% the generator stops, making sure that the remaining battery capacity can be charged by the PV panel energy the next day.
1
d i s c h a r g e
2
d i s c h a r g e
...n
n+1
disc harg e
Partly chage
c h a r g e
disc harg e
Partly chage
c h a r g e
disc harg e
Partly chage
charge
24h
?h
- 20 -
4. CASE STUDY
Site Location: In the equatorial zone with a stable and predictable regional weather pattern. Initial site power configuration : Off-grid BTS site powered with 1+1 15KVA diesel generators, running 24 hours a day, 7 days a week. A small lead-acid battery bank connected to the DC power system for emergency backup only. Stated site load profile: The average load was stated as ~2.5kW and autonomy requirement was 3 days. Upgrade project target: The initial requirement was to upgrade the site to be partly powered by PV panels to reduce the OPEX with a limited CAPEX. Upgrade activities The site was upgraded as follows: - Original gen-sets removed and replaced with a single 20KVA gen-set. - DC power system upgraded to 18kW - 3kW solar solution installed. - Upgraded the battery bank to 3000Ah (with OPzV) - All components integrated and monitored by the DC power system controller. Gen-set cycling was enabled, with an initial DOD value set at 30%. Studying the results from the first months showed that the average load was 40% less than specified, so the actual autonomy was approximately 5 days. After discussion with the battery supplier the restart charging level of the batteries was increased to 50% DOD, resulting in longer intervals between starting of the diesel generator.
Conclusions
With the current configuration the energy supply split for a collection of sites in August 2009 is shown in
Figure 10. Approximately 21% of the energy used on the sites was delivered by PV panels. The remaining energy was supplied by the diesel generator.
Gen set Solar
79 %
- 21 -
Figure 11 shows a comparison of diesel consumption between the original configuration and the Eltek Valere hybrid configuration. The fuel reduction of 75% has been confirmed by the operator, reducing the monthly carbon footprint by 10 ton, and significantly increasing the diesel generator service interval.
Fuel usage, August 2009
6000
5000
4000
Diesel [l]
3000
2000
1000
For this project, the payback time for the extra investment will be approx 3 years, including battery replacement after 7 years.
- 22 -
REFERENCES
Electric Power Monthly, November 2007 Edition (Energy Information Administration) Verizon Corporate Responsibility Report 2006 Verizon Communications Green House Gas Emission Reduction Initiatives (on Clean Air, web site) Telefonica CR Report 2006 NTT Group Environmental Protection Activity Report 2004 Energy Information Administration Qwest Power Engineering Organization - Central Office Rectifier Replacement Study